Sizing a Boiler for a Brewery

The most important part of the brewery steam system design is to size the boiler properly. An oversized boiler can result in frequent cycling while an undersized boiler may never be able to meet the temperature requirements of the brewery. Both of which will adversely affect the brewing process. A steam boiler should be sized according to the connected load. The connected load includes all the vessels and tanks as well as the piping. The manufacturer of the brewing equipment should provide the Btu consumption of their equipment. Another sizing consideration is the planned expansion of the brewery. Since the market is brewing and distilling market snowballing, the boiler you design today may be undersized next year. If you do an internet search, there are many rules of thumb for sizing a brewery boiler including:

50,000 Btuh per barrel of capacity,1-2 Boiler HP (BHP) per brew barrel,1 BHP per barrel for smaller brewers and 2 BHP for brewers per barrel with large hot liquor tanks. As with most rules of thumb, they may or may not be accurate for the facility. According to brew industry design expert, Blaine Clouston with Simplified Stainless, the equipment manufacturers generally ensure the heating equipment to meet the following:

Brewkettle heating - 1.5 degree F/minute

Brewkettle, evaporation -  5- 6%/hr

Mash Vessel Heating  - 1.5 degree F/minute

Hot Liquor tank - ability to heat water 1.5 times the brewhouse size in 4 hours. Example; a 10 barrel system would typically use up to 15 barrels in hot liquor.

Based on his extensive engineering background, Mr. Clouston has some shortcuts which he feels are more accurate for sizing:

Brewkettle Heating and Boiling = 32,000 Btu/Hr/bbl

Hot Liquor Heating from 60-175F in 4 hours = 19,500 Btu/Hr/bbl

Mash Vessel Heating = 29,000 Btu/Hr/bbl

Bbl = Barrel

 

 

Other Brewery Boiler Sizing Options

According to the Master Brewers Association of the America's book, Brewing Engineering and Plant Operations, the following are the sizing guidelines it recommends: 

50,000 Btuh per barrel of capacity. 

Wort* heating prior to boiling 

Btu's required to heat 1 barrel of wort from 1500F to 2120F in one hour. 

1 bbl x 31 gal/bbl x 8.34 lb/Gal x (2120F -1500F) x 1 Btu/F0 = 16,030 Btu/Hr.

Wort* boiling in a kettle

Energy required to turn wort at 212 to start to boil. 

1 bbl x 31 gal/bbl x 8.34 lb/Gal x 0.05 evaporation/hr x 970 Btu's/lb = 12,539 Btu/Hr.

Btu's required per barrel of Wort*

Amount of energy needed when boiling Wort in a Kettle. 

Btu/Hour = 1bbl x 31 gal/bbl x 8.34 lb/ Gal x 970 Btu/ Lb

*Wort is the liquid extracted from the mashing process during the brewing of beer. 

Bbl = Barrel

Additional sizing considerations 

Part of the sizing calculation is whether the steam-consuming components will be operated separately or simultaneously as this affects the boiler and pipe sizing. Another item to consider is the energy required to heat all the pipes from a cold start. A rule of thumb is to add 15-30% of the processing load for the cold piping, depending on the distance the steam must travel to the process. Brewery elevation must also be factored into the design as well.

Boiler Efficiency  

When your sizing is complete, you have to factor in the efficiency of the boiler as the heat load of the plant will be the output of the boiler. Most steam boilers will have an efficiency range between 80% and 85%. 

For ease of calculation, let us look at the heating requirements for a 10 barrel brewery with simultaneous operation.

Brewkettle 32,000 Btuh X 10 barrels = 320,000 Btuh

Hot Liquor 19,500 Btuh X 10 barrels = 195,000 Btuh

Mash Heating 29,000 Btuh X 10 Barrels= 290,000 Btuh

 SUBTOTAL = 805,000 Btuh

Cold piping loss 25% =  201,250 Btuh

Boiler Net Output =  1,006,250 Btuh

Boiler input @ 80% Boiler Efficiency = 1,257,813 Btuh

Boiler input @ 82% Boiler Efficiency = 1,227,134 Btuh

We would need a boiler with an input of about 1.2 Mil 

 

Would you like to learn more from Ray Wohlfarth? Check out his seminarsbooks, and blog about brewing with steam.

Categories

Leave a comment

Related Posts

Freezing Univentilator Coils

I had written a story for Plumbing & Mechanical a while back about a fella in Canada who sent me this email: "Our problem is that five out of hundreds of univentilator co...

Published on 05/08/2023 3:15 PM by Dan Holohan
Posted in Steam Heating
near boiler piping
Dry Steam Is The Goal

I love all the advances taking place in the world of hydronics, but I’m still seeing plenty of steam systems out there in our older cities, so knowing about dry steam wil...

Published on 03/01/2023 10:29 AM by Dan Holohan
Posted in Steam Heating