Boiler-Safety Controls
When looking at a commercial boiler, there are many controls mounted on and around it. It reminds me of a Christmas tree with ornaments hanging from it. The function and duty of these controls are sometimes confusing.
Operating Control
The operating control is the main control for the boiler. This control will be set for the desired water temperature or steam pressure of the system.  In most hydronic applications, the operating control will be set for 1800F. The industry has adopted 1800F as the official Design Water Temperature. Heating systems and equipment were designed to operate at full capacity using 1800F water.  Be careful if the control is set for lower than 1400F as the boiler flue gases would condense. Many manufacturers will void their warranty if the boiler water temperature is below 1400F. When the flue gases condense, acids are released which will attack the piping, flue and chimney.
On steam systems, the operating control is typically set for 2 psi. The controls should be installed on a siphon or pigtail. This protects the control from live steam by using a water seal.
The operating control is an automatic reset type control. That means that the control will automatically start once the temperature or pressure drops to a predetermined temperature or pressure.
Limit Control
The limit control has the same responsibility as the operating control but with two distinct differences. The first is the set point. The set point for the limit control is set at a higher temperature or pressure than the operating control. The other difference is that the limit control is a manual reset control. That means that when the temperature or pressure reaches that point, it will open and interrupt electric service to the burner. The control will require a button to be depressed to reset the control to allow operation again.
Many installers wonder why the limit control is a manual reset and not an automatic reset control.   Well, consider that your operating control is set at 1800Fand the limit control is set at 2100 F. If the boiler temperature raises high enough to trip the limit control, you can be fairly sure that the operating control is not working. The manual reset feature is designed to get someone into the boiler room to investigate.
Modulating Control
The modulating control should be set for a temperature or pressure that is slightly lower than the operating control. For example, it may be set for 175 degrees and the operating control is set for 180 F.  When the water temperature gets to the modulating control set point or 175 as above, the burner will drop to low fire.  When the water temperature or pressure drops, the modulating control will drive the burner to somewhere between low fire and high fire. Modulating burners are used to better track the temperature or pressure requirements of the building. They also reduce cycling.
Low-Water Cutoff
The low water cutoff is the leading mechanical cause of boiler accidents. The low water cutoff is mounted at an elevation that is above the lowest possible water level of the boiler.  On hydronic systems, it is common to have one installed in the piping above the boilers.  If the low water cutoff is connected to the system piping with nipples or pipes, valves cannot be installed in the piping to allow isolation of the low water cutoff and the system.
The older type low water cutoffs used to use an internal float that would track the water level of the boiler.  Many of the newer types of low water cutoffs use a probe type sensor for the low water cutoffs.
Commercial steam boilers require two low water cutoffs. The primary low water cutoff on a commercial steam boiler usually has two functions. It is typically referred to as a low water cutoff / pump control. When the water level drops in the boiler, the first set of contacts will start a boiler feed pump and / or open a feed water valve. If the water level continues to drop, the low water cutoff will interrupt the electrical service to the burner, shutting off the burner.
If the level continues to drop inside the boiler, the auxiliary low water cutoff will trip, cutting power to the burner. The auxiliary low water cutoff should be a manual reset style. The auxiliary low water cutoff will be installed at a lower elevation than the primary low water cutoff.
Flow Switch
Water tube or coil type boilers that rely on flow for proper operation use a flow switch instead of a traditional low water cutoff. Some of these boiler types may be referred to as copper finned boilers.  I prefer a low water cutoff to be installed in the system piping for these systems even though they are not required for code compliance.
Primary Control
The primary control or flame safeguard assures that the burner operates correctly.  It will typically be installed inside the burner control panel.  Many feature a manual reset switch on the control.
Gas-Pressure Switch
Some boilers require gas pressure switches to meet code compliance. The gas pressure switches are to verify that the gas pressure is within a safe range.  If the gas pressure is too low or too high, the burner will not operate correctly. Several years ago, a main gas regulator failed in Chicago. People were reporting five foot tall pilot flames on their stoves. The high gas pressure switch will be located on the burner head. The low gas pressure switch will be on the gas train downstream of the gas pressure regulator.
Would you like to learn more from Ray? Check out his seminars and books.
Posted in Steam Heating
Freezing Univentilator Coils