Understanding Flame Safeguards
As I accompanied my friend from the local utility company into the boiler room, I noticed that the covers were off all the electrical boxes and wires were hanging out of them. That is never a good sign.
The purpose of my visit was to offer some suggestions to help the client lower their fuel costs. They were having a difficult time paying their gas bill. Our meeting included the Director of Maintenance and his boiler maintenance staff. As we were talking with the maintenance personal in the boiler room, the lead boiler tech said that he needed to start the boiler. I watched as he walked to one of the large boilers and opened the door to the base of the boiler. He took a broom, lit the bristles on fire and shoved the lit broom inside. His next task froze me. He opened a 2 ½” manual gas valve and the burner started with a soft “Whoom.” Flames were visible from the opening of the boiler. He pulled the broom out and stomped on it to extinguish it.
I gasped loudly and the maintenance man laughed. “Why do you do that?” I asked.
“Aw, the flame safeguard is defective. Do you know how much those things are?” he answered.
“So you bypassed it?” I stammered.
“Yep, been like that for months now. Whenever we need heat, we just light the broom and off we go. You gotta be careful sometimes as that flame will singe your hair.” he answered. I do not know whether I was more concerned with how they “lit” their boiler or that they thought this was ok to do that.
 The maintenance man in the above story is correct. A flame safeguard is much more expensive than a simple thermocouple. Some maintenance people will ask why the industry has gone away from thermocouples. The main reason is response time. The response time for a thermocouple is between one and three minutes. A flame safeguard will respond within four seconds. It may not seem like such a big deal but consider this. If the flame goes out on a 1,000,000 Btuh boiler with a thermocouple and the thermocouple response time is 2 minutes, the boiler will have about 16 cubic feet of gas and mixed with the combustion air would equal about 240 cubic feet of explosive mixture. Contrast that with a boiler with a modern flame safeguard with a 4 second response time. It would allow slightly more than 1 cubic foot of gas and the explosive mixture of air and gas would be about 16 cubic feet, about 94% less.
 During my seminars, I am often asked how a flame safeguard operates. A flame safeguard is a sophisticated control that will monitor the fuel burning equipment to assure safe operation. On a call for heat, the flame safeguard will start the burner fan. The blower operation is verified with a sensing device, usually a pressure switch. If the burner is a modulating one, the burner air intake damper will open. This is called “Pre-Purge” The fan will operate for anywhere from 30 seconds to several minutes. This is to “purge” the boiler combustion chamber of any unburnt fuel. The purge will be enough to provide four full air changes in the combustion chamber. After the pre-purge, the pilot will light. The flame safeguard will check the pilot flame to make sure that it is safe and stable. If the burner is a modulating one, it will drive to a low fire position.
At that point, the main gas valve will open. The flame safeguard will continually monitor the flame until the call for heat has ended. Some older burners used a “Post-Purge” to void the combustion chamber of any unburnt fuel after the call for heat. This is wasteful as it will take heat from the boiler and exhaust it up the stack.
Another consideration with flame safeguards is the flame sensing types. There are commonly four flame sensing devices. They include flame rectification or more commonly known as a flame rod, photo cell, ultraviolet, and infrared. The flame rectification is the most common sensing device. Flame rectification uses a theory that a flame will actually conduct electricity. I wonder how many singed eyebrows there were when they tried to test that theory. A small electrical charge will be sent to the flame rod. If a flame is present, the current will travel through the flame to ground. If the ground is sensed, the main gas valve will open.
The photo cell, common for fuel oil burners, looks for the visible light of a flame. When light is present, the sensor will emit electrons and tell the flame safeguard that a flame is present.
Infrared flame sensors can be used on either gas or fuel oil. It senses the infrared radiation that is present in a flame. It can sometimes be fooled by hot refractory inside a boiler.
Ultraviolet flame sensing tests for the ultraviolet waves that are present inside a flame. The UV sensor will not respond to any visible light. It can be fooled by hot refractory, spark ignition, gas laser, sun lamps, germicidal lights and a bright flashlight.
The best way to check the operation of a flame safeguard is with a meter. The following table will show you the suggested readings for different flame safeguards.
Typical Flame Safeguard Signals
Fireye
Model
Average Flame Signal
UVM
4.0-5.5 VDC
TFM
14-17 VDC
D-10/20/30
16-25 VDC
E-100/ 110
20-80 VDC
E-100/E110 with EPD Programmer
4-10 VDC
M Series II
4-6 VDC
Micro M Series
4-10 VDC
Micro M Series w Display
20-80 VDC
Honeywell
Model
RA890
2-6 mA DC
R4795
2-6 mA  DC
R7795
2-6 mA  DC
R4140
2-6 mA  DC
R4150
2-6 mA   DC
BC7000
2-6 mA  DC
RM7890
1.25-5 VDC
RM7895
1.25 VDC
RM7840
1.25 VDC
RM7800
1.25 VDC
Typical Flame Safeguard Signals Siemens
Gas Burner Controls
Model
Flame Signal
LFL with UV sensor QRA
Minimum 70 uA DC
100-450 mA DC
Typical
LFL with Flame Rod
Minimum 6 uA DC
20-100 mA DC
Oil Burner Controls
Model
Flame Signal
LAL1 with photoresistive detector, QRB1
95-160 mA DC
LAL1 with blue-flame detector, QRC1
80-130mA DC
LAL2/LAL3 with photoresistive detector, QRB1
8-35 mA DC
LAL2/LAl3 with selenium photocell detector, RAR
6.5-30 mA DC
LAL4 with photoresistive detector, QRB1
95-160 mA DC
LAL4 with blue-flame detector, QRC1
80-130 mA DC
mA = Micro Amp
Would you like to learn more from Ray? Check out his seminars and books.
Posted in Steam Heating
Freezing Univentilator Coils